11-17-2021, 08:34 PM | #1 |
Senior Member
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
|
Extension Cord type for Generator use?
I just purchased a 6000 kw portable generator. Generator has 4 120v connections. One of the connections will be used powering my pellet stove (going to keep this separate from others). One connection will power a refrigerator/freezer (probably keep this on a dedicated line), and two other connections will be used to power several lights and charge phones & PC's.
Based on my description what 'gauge' extension cords do I need to connect to generator for these devises ? 16/3...or 14/3 ? The distance from generator into house will not be more than 75'. Thoughts? |
The Following User Says Thank You to bigdog For This Useful Post: | ||
MBNeckguy (11-17-2021) |
11-17-2021, 09:48 PM | #2 |
Senior Member
Join Date: Jun 2021
Posts: 2,912
Thanks: 2
Thanked 523 Times in 431 Posts
|
When used this way, it depends on the amperage that will run down each.
And you have to allow for surge, like when a refrigerator first starts its cycle. |
11-17-2021, 10:16 PM | #3 |
Senior Member
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,409
Thanks: 304
Thanked 117 Times in 94 Posts
|
Thanks John, will take your comment into consideration.
Forgot to add, I plan to plug pellet stove into a power-strip with surge protector, then that surge protector into generator extension. Don't want any surges going back to pellet stove to fry circuit boar. Just a FYI, my Champion generator has a surge protection feature built into the system, it's referred to as a 'volt guard'. Here is the description of the volt guard device from the company site: "Champion's Cold Start Technology ensures a quick start in cold weather, the Volt Guard™ built-in surge protector prevents overloads and keeps your equipment safe from spikes in voltage and the voltmeter allows you to easily monitor power output anytime." Kinda cool ! |
11-17-2021, 11:23 PM | #4 |
Senior Member
Join Date: Jul 2014
Posts: 5,939
Thanks: 1,152
Thanked 1,959 Times in 1,210 Posts
|
6000kw or 6000 watt? I'm assuming the latter.
Why go through the trouble of running multiple cords and separate connections? If the machine has a 220v output, run it directly to your panel with a mechanical interlock and then you can run any of the circuits in your house. Because I am fully electric—heat, clothes dryer, water heater, etc.—I can't run my whole house off a portable generator, but it's a breeze to click off those circuits (that I've marked with pink stickers) and electrify the rest, which means any lights, fridge, garage door openers, computer network gear, etc. can be used. Much easier than running multiple cords, etc. Sent from my SM-G950U using Tapatalk |
11-17-2021, 11:29 PM | #5 |
Senior Member
Join Date: Apr 2004
Location: Bear Island
Posts: 1,757
Thanks: 31
Thanked 429 Times in 203 Posts
|
The basic answer is use 12/3 for 20 amp (2400 watt) and 14/3 for 15 amp (1800 watt). However the temperature rating of the wire is the important thing. If you use high temp cord rated at 90 degrees C you can get more amps through it safely. Another consideration is you should go up a wire size when going more than 50 feet.
Simple answer 12/3. |
The Following User Says Thank You to Bear Islander For This Useful Post: | ||
bigdog (11-18-2021) |
Sponsored Links |
|
11-18-2021, 01:10 AM | #6 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
Quote:
But I agree with what you said and you can still do what you said with a 120V generator. That’s what I did. None of my 220V appliances are critical. I moved all the critical circuits onto the same phase and just feed that. Agree with the 12/3 recommendation. If the generator has a 30A 120V you should go 10/3 and feed the panel with it. You can get an external generator panel that you move critical circuits too. Or one of those “quicky” interlocks for your main panel if you can find one that fits your panel. |
|
11-18-2021, 06:26 AM | #7 |
Senior Member
Join Date: Mar 2008
Location: Welch Island and West Alton
Posts: 3,211
Thanks: 1,167
Thanked 1,999 Times in 913 Posts
|
|
11-18-2021, 07:13 AM | #8 |
Senior Member
Join Date: Nov 2013
Posts: 391
Thanks: 20
Thanked 130 Times in 93 Posts
|
12/2 vs 12/3
12/2 wire has a total of 3 conductors and is used in 110 volt applications. It has 3 conductors…black is hot, white is neutral and the bare conductor is ground.
12/3 wire has 4 conductors and is most commonly used in 220 volt applications. It has 4 conductors… both black and red are hot, white is neutral and the bare conductor is ground. If you are plugging into the 110 volt outlet on generator you should use 12/2 cords. Good luck! |
11-18-2021, 07:37 AM | #9 | |
Senior Member
Join Date: Apr 2004
Location: Kuna ID
Posts: 2,755
Thanks: 246
Thanked 1,942 Times in 802 Posts
|
Quote:
It is critically important to understand what the generator can handle far as output both steady state and startup. Equally important in understanding the draw of what is being plugged in, and how many really both to know that? When I wired my house I put in a sub panel and moved only the circuits I needed to power into it. That gave me some level of confidence I would never overdraw my generator's capacity. Of course when powering outlets anything can be plugged in but I just calculated the total amount of draw possible for the circuit and went with that. |
|
11-18-2021, 09:52 AM | #10 | |
Senior Member
Join Date: Jun 2021
Posts: 2,912
Thanks: 2
Thanked 523 Times in 431 Posts
|
Quote:
When a refrigerator first starts up, it uses more power than once it is running. This causes a quick spike in the draw on the wire. |
|
The Following User Says Thank You to John Mercier For This Useful Post: | ||
bigdog (11-18-2021) |
11-18-2021, 09:57 AM | #11 | |
Senior Member
Join Date: Jul 2014
Posts: 5,939
Thanks: 1,152
Thanked 1,959 Times in 1,210 Posts
|
Quote:
The bigger danger is when people backfeed through a 220v outlet such as an electric clothes dryer or stove. That can leave the main open and backfeed the power lines resulting in major potential damage and death. Using a (properly installed) mechanical interlock, the real only danger is having too many circuits on at the same time, and that's easily remedied by a few stickers. The person looking to do this would, most likely at least, understand that much. Sent from my SM-G950U using Tapatalk |
|
The Following User Says Thank You to thinkxingu For This Useful Post: | ||
NH.Solar (11-19-2021) |
11-18-2021, 12:36 PM | #12 | |
Senior Member
Join Date: Apr 2004
Location: Bear Island
Posts: 1,757
Thanks: 31
Thanked 429 Times in 203 Posts
|
Quote:
To connect a portable generator you must be using flexible cord which is different than wire. A 12/3 flexible cord has a white, black and green insulated conductors. |
|
11-18-2021, 01:07 PM | #13 |
Senior Member
|
Ya-knows ...... for a price like 99-cents you can get a white extension cord at that Saint Vincent de Paul thrift store ...... made with 16 or more likely with 18-gauge lamp cord ..... which is totally good-to-go for any and all your residential home heating and lighting needs ...... no worries! .....
__________________
... down and out, liv'n that Walmart side of the lake! |
11-18-2021, 02:37 PM | #14 |
Senior Member
Join Date: Apr 2004
Location: formerly Winter Harbor, still Wolfeboro
Posts: 1,130
Thanks: 284
Thanked 480 Times in 271 Posts
|
Extension cord type for generator use
Safety is the name of the game when using electricity, and your remarks are unsafe, irresponsible, and, not funny. If you want to make a joke, fine, but make it about something that can't kill you. This thread was started by someone with a legitimate question, and it doesn't deserve an illegitimate answer.
|
11-19-2021, 06:17 AM | #15 |
Senior Member
|
Well ....... for $59.25 ........ walmart.com has a neon pink 12/3 50' extension cord ....... good to keep that outdoor hot tub humming when the power is down, and the generator comes alive.
Hey look ...... the hot tub is still going ...... whoopeee! ..... and it is HOT ..... grab me a beer! .... gotta love the winter in New Hampshire ..... ..... just keep one eye on that tip-up orange flag, out there Off-topic ..... have you seen the giant black spider on the WeirsCam!
__________________
... down and out, liv'n that Walmart side of the lake! |
11-19-2021, 09:21 AM | #16 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
Quote:
You can feed the house or sub panel with 120V. It’s just not as flexible/ideal. Even with a small generator sub panel you can still over load the generator. |
|
11-19-2021, 10:02 AM | #17 |
Senior Member
Join Date: May 2021
Posts: 339
Thanks: 50
Thanked 92 Times in 66 Posts
|
Good advice was given, for the OP's direct question use 12 gauge regardless of amp load due to his saying he may run 75 ft. Plus, since you said the pellet stove is plugged into a power strip, there's always the possibility that something else gets plugged in.
I TOTALLY agree with those suggesting correctly done generator wiring. It isn't expensive, gives a lot of comfort in the case of an extended outage, and is SAFE. You can do the sub panel as many suggest, I've chosen to do the full breaker panel capability where all circuits are available. |
11-20-2021, 12:25 AM | #18 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
Quote:
One thing you do need to be careful of is going above 80% of designated amps. Which is possible even with a sub panel. For continuous load you probably want to keep it under 50% capacity of the generator. Leave the rest of the headroom for appliances that will surge. Like someone said in the other thread. You do have to have some understanding of what’s going on. How some appliances surge. How much surge the generator can handle etc. What ever you do, don’t run a microwave. Even small one would make my 4000 watt (non inverter type) generator go nuts. It’s a very odd load. If the lights dim (or watch the volt meter going under say 105V) or generator is straining , back off on the load. |
|
11-20-2021, 10:44 AM | #19 |
Senior Member
Join Date: Dec 2016
Posts: 1,867
Thanks: 192
Thanked 590 Times in 395 Posts
|
I have six circuits wired on a 5k. Three are must have’s. Septic, well, and furnace. After that, it’s fridge and a few lights
Sent from my iPhone using Winnipesaukee Forum mobile app |
11-20-2021, 11:02 AM | #20 |
Senior Member
Join Date: Jun 2021
Posts: 2,912
Thanks: 2
Thanked 523 Times in 431 Posts
|
Why does your septic need power?
Serious question. |
11-20-2021, 11:40 AM | #21 |
Senior Member
Join Date: Dec 2016
Posts: 1,867
Thanks: 192
Thanked 590 Times in 395 Posts
|
|
11-20-2021, 12:18 PM | #22 | |
Senior Member
Join Date: May 2021
Posts: 339
Thanks: 50
Thanked 92 Times in 66 Posts
|
Quote:
I've always run a microwave during outages, with no problem. |
|
11-20-2021, 12:52 PM | #23 |
Senior Member
Join Date: Jun 2021
Posts: 2,912
Thanks: 2
Thanked 523 Times in 431 Posts
|
The refrigerator uses a lot of amperage on start-up, but the generator should have the capacity... as long as the extension cord does.
Newer appliances are gaining efficiency partial by changing how they start to reduce that initial start-up load. |
11-21-2021, 01:25 AM | #24 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
Quote:
Twice the work requires the square in power. Like for a pool my pump would run like 6 hours a day. But if I ran it half speed for twice as long (12 hrs) it would take half the amount of total power even though it’s running twice as long. Now cut the speed in half again and double time again I’m at 24hrs and use 1/4 the total power for the same amount of water filtered. Refrigerators, AC/Heat Pumps, Water Pumps all are moving in this direction. They run continuously at the speed needed based on the demand. Instead of a burst at high speed for short bursts of time. |
|
11-21-2021, 01:38 AM | #25 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
Quote:
When I’m on generator I’m surprised how little I can comfortably get by with. Here is a typical days usage. Both working from home. Never broke ~1600 watts. Do I really need a 8000 watt generator. Last edited by mswlogo; 11-21-2021 at 09:21 AM. |
|
11-21-2021, 10:53 AM | #26 | |
Senior Member
Join Date: Jun 2021
Posts: 2,912
Thanks: 2
Thanked 523 Times in 431 Posts
|
Quote:
Same thing with the ''smart thermostat'' with the furnace in another discussion. Explaining the difference between the old/new doesn't really help the OP, as it isn't something they really control. The only difference being that the newer is more susceptible to supply variation that can damage the unit. |
|
The Following User Says Thank You to John Mercier For This Useful Post: | ||
mswlogo (11-21-2021) |
11-21-2021, 10:59 AM | #27 |
Senior Member
Join Date: May 2021
Posts: 339
Thanks: 50
Thanked 92 Times in 66 Posts
|
That's a great setup, and you are right, in your case no need to upsize the generator.
At my home I have NG heat and hot water, but electric stove. Not using the stove is an obvious way to dramatically reduce capacity needs, but if you use both microwave and toaster oven instead it adds up. An electric stovetop burner is about the same wattage as a toaster oven. 6500 watts covers the house nicely, if we wanted to cook Thanksgiving dinner then you'd need 8000-9000 watts. I realize it's no hardship to go without using the oven for a few days! Obviously I should have qualified my statement that it depends on house configuration, thanks for that clarification. |
The Following User Says Thank You to LikeLakes For This Useful Post: | ||
mswlogo (11-21-2021) |
11-21-2021, 04:48 PM | #28 | |
Senior Member
Join Date: Jun 2014
Posts: 660
Thanks: 196
Thanked 222 Times in 143 Posts
|
Quote:
"Newer appliances are gaining efficiency partial by changing how they start to reduce that initial start-up load." If that was meant to simplify conversation that's fine by its misleading, confusing and basically wrong. That statement is implying by removing startup surge that that it is how they are more energy efficient. That's simply not the case. Startup surges were insignificant with regard to consumption because they were so short. But as I think you meant too convey by eliminating startup surges you reduce the cost in handling "peak loads". You can get by with smaller generator, smaller circuits because you can focus on the max continuous load only. For example I changed my AC pool pump two decades ago from single speed AC to two speed AC pump. They both still had the same peak surge load. But I still got the same efficiency as a modern DC variable speed pump by running the pump at 1/8 the speed (low). That's how I gained huge efficiency with no change in surge. On side note, whether the appliance is an old or new it should have a tag listing peak load. Likewise the generators all list peak and continuous load. And the major label on the generators that say like 8000 Watt generator is usually the peak capacity and not continuous load. If you wanted a simple and correct version of what you meant "A bonus in newer appliances gain in efficiency they have all but eliminated large start up surges". |
|
Bookmarks |