Latest estimate to replace my boiler with coil with same type, came in around $5500, materials and labor. HVAC company gave me the estimate but did not break-out line items for boiler cost and labor hrs. have since asked for that info.
This includes all new burner setup, piping valves, etc, and disposal of old boiler. They added extra 5 yrs to warranty and 2 yrs of annual cleanings to sweeten the deal. HVAC contractor is a HUGE dealer out of Concord, with lot's of experience and a great reputation. Labor per hours is pretty much standard $75-100 hr per man. Boiler costs, they tend to pad, and build in fluff ! I have a oil burner guy in Mass, who can do the job probably for less, but would require him to, come to property here and do the job same day. I would also have to purchase the boiler myself and have delivered to property. In the end I may only save $500-700 +/-. Not sure it's worth the trouble ? |
|
|
|
|
|
#2 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
|
|
|
|
|
|
|
#3 |
|
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,953
Thanks: 484
Thanked 703 Times in 393 Posts
|
Were I you I would have the coil cleaned and replace the mixing valve if the boiler is not leaking. That should cost a few hundred bucks. A lot better than $5,500. Once they flush it out I doubt you would have any sediment issues. Personally I hate coils and would never install another were I putting in a new boiler. In fact, my coil started acting up on my summer house and I put a super stor in, worth every penny in my opinion. That was about 6 years ago, old boiler is still going strong. But if money is an issue, I would have the coil cleaned and put a new mixing valve in.
I don't believe in replacing boilers until they start leaking, any increase in efficiency is small compared to the cost of replacement. I like to get every last penny out of stuff. |
|
|
|
|
|
#4 |
|
Senior Member
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,459
Thanks: 357
Thanked 126 Times in 100 Posts
|
Biggd,
My boiler is a Weil McCalin (coil type) 'contractor grade' for condo, 2 zones, about 100,000 btu's. ITD, To answer your question regarding removing and replacing the coil, it's sort of a crap shoot ! By that I mean if the bolts on the plate housing the coil are rusted, they could snap off, then the bolts would have to re-tapped, running up the cost. The coil costs about $450, with maybe 2-3 hours work depending on unforeseen issues during replacement, and no guaranty it won't leak at that connection after work completed. So bottom line, about $700-800, and I still have a 25 yr old boiler..... I could be throwing good money to bad on this option, a roll of the dice ! A lot of "if's" to replacing coil ! So difference between coil replacement and new boiler about $4000-4500, still a lot of money, but I'll be able to sleep at night, and know I have hot water for another 25 yrs., but I'll be dead by then !
|
|
|
|
|
|
#5 | |
|
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,953
Thanks: 484
Thanked 703 Times in 393 Posts
|
Quote:
|
|
|
|
|
| Sponsored Links |
|
|
|
|
#6 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
|
|
|
|
|
|
|
#7 | |
|
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,953
Thanks: 484
Thanked 703 Times in 393 Posts
|
Quote:
A new boiler can crap out too, I monitor my house for temperature in the winter. I went through this same scenario 5 or 6 years ago, my boiler is still going strong, but it's time is coming. |
|
|
|
|
| The Following User Says Thank You to ITD For This Useful Post: | ||
SteveO123 (05-04-2017) | ||
|
|
#8 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
Also, flushing out a heating coil almost never works and a heating contractor would never guarantee it would. 9 times out of 10 you would be throwing money away. Just like the $800 I spent on an emergency repair on my 30 year old boiler the winter before I replaced it. And changing the mixing valve will do nothing if the water coming out of the coil is not hot enough. |
|
|
|
|
|
|
#9 | |
|
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,953
Thanks: 484
Thanked 703 Times in 393 Posts
|
Quote:
|
|
|
|
|
|
|
#10 |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
My boiler at my residence in Ma is over 20 years old. I have had at least one issue every year for the past few years where it has stopped working on the coldest nights. I'm milking it because I plan on selling in a few years when I retire so the next guy can worry about it. No heating coil in that one, I have a external storage tank. Everyones situation is different.
|
|
|
|
|
|
#11 | |
|
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
Quote:
There is no boiler with a tankless coil that will get over 55-60% efficiency or is there a boiler that will get you an 89% efficiency! I'm confused where everyone is getting these numbers from? You are right when you suggest never to get the coiled cleaned... your wasting your money. Unfortunately many heating "professionals" aren't professional they'll say and do what ever to get your money... |
|
|
|
|
|
|
#12 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
|
|
|
|
|
|
|
#13 | |
|
Senior Member
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,669
Thanks: 3,282
Thanked 1,132 Times in 814 Posts
|
Quote:
Check out: https://www.energystar.gov/products/...icient/boilers Unfortunately there are no oil burners on the list nor is there and on-demand hot water on oil. A friend of mine replace his oil burner and electric hot water heater with propane condensing boiler with on demand. His energy bill is less from prior year even though propane is a little more expensive. It's in the efficiency.
__________________
Someday may never be an actual day. |
|
|
|
|
|
|
#14 |
|
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,953
Thanks: 484
Thanked 703 Times in 393 Posts
|
There are condensing oil boilers that get over 90% AFUE.
I've had a coil cleaned and it worked out just fine for about 5 or so years, then I had it cleaned again and it was good for another 5 or so years. Money was an issue at that point in my life. Then the boiler cracked (Burnham) and I replaced it, I put in a Superstor at the same time and haven't had a problem since. Biggd wants a new boiler, and that is great, go for it. The payback numbers are pretty simple math, for an engineer anyway, they may not be perfect, but I suspect they are within 10% at least of being accurate. If you go from 55% to 75% then it would take about 18 years to pay back a $5,500 boiler if you burn about 1,000 gallons per year, which should be pretty close for 100,000 btu boiler and a reasonable house. Unless I screwed up my math, I've been wrong before, but please show me the correct way if I'm wrong. As far as your issues with your boiler at home Biggd, I suggest you change your contractor. Oil burners aren't rocket science, they are actually pretty simple, especially a contractor grade boiler, as long as you clean them annually and change the parts your service guy recommends, you should not be having problems. I have two houses, the last emergency service call I had was because Fuller ran me dry on automatic delivery. I fired them that day because they would only bring me 10 gallons of oil. That was a few years ago. The guy servicing your boiler makes a big difference. |
|
|
|
|
|
#15 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
|
|
|
|
|
|
|
#16 |
|
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
Curious what you guys are referring to when you say to "clean" your coil. Do you mean internally or the outside of the coil if it has mineral deposits accumulated? Wondering how you clean a coil internally. My Burnham boiler is over 25 years old. I replaced the coil at least 10 years ago as it was leaking into the boiler water. No issues since.
__________________
SIKSUKR |
|
|
|
|
|
#17 | |
|
Senior Member
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,953
Thanks: 484
Thanked 703 Times in 393 Posts
|
Quote:
|
|
|
|
|
|
|
#18 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
|
|
|
|
|
|
|
#19 |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
On another subject. I've had quite a few friends that have been talked into those new gas instant boilers the size of a suitcase that hang on the wall. Everyone of them have had problems with them every year. They are very efficient when they are working. One of them had to have his replaced after only 5 years. The unit was under warrantee but not the installation. This is the way the industry is going. Just like every other appliance made today, they are only made to last until the warrantee is up. You will never get 30 years out of one of these units.
|
|
|
|
|
|
#20 | |
|
Senior Member
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,669
Thanks: 3,282
Thanked 1,132 Times in 814 Posts
|
Quote:
Most if not all the replacements are condensing boilers. Any complaints in the last few years were from faulty installations, faulty zone switches, and circulators. They have nothing to do with the boiler manufacturers. They are added on by HVAC. Seems like the add ons are giving the boiler manufacturers a bad rap. In fact my HVAC guy even told me that when I had concern about the quality of the Rinnai. Talked to a number of Rinnai owners that had their unit for a decade or more have confirmed this fact.
__________________
Someday may never be an actual day. |
|
|
|
|
|
|
#21 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
I see the attraction of not having a dedicated space for a boiler and hot water tank where this unit does both and just hangs on the wall out of the way. And builders love them because they don't need expensive chimneys cutting down the costs of a new house. But I wouldn't install one in my house unless I had limited space issues. Last edited by Biggd; 05-05-2017 at 08:50 AM. |
|
|
|
|
|
|
#22 |
|
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
No opinion either way here but with today's high efficiency boilers there really is no need for a chimney unless you don't want a forced draft system. Heck a lot actually have pvc for exhaust flue.
__________________
SIKSUKR |
|
|
|
|
|
#23 |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
The real expensive homes still have brick or stone chimneys and real wood fireplaces. A brick or stone chimney can add another 10 to 20K to the build so unless it's a multi million dollar house you won't see many anymore. The last house I built 10 years ago a brick chimney with two flues and one fireplace cost me 12K.
|
|
|
|
|
|
#24 | |
|
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
Quote:
__________________
SIKSUKR |
|
|
|
|
| The Following User Says Thank You to SIKSUKR For This Useful Post: | ||
SteveO123 (05-18-2017) | ||
|
|
#25 |
|
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
The only thing that can be installed legally with pvc is a gas furnace, unless it's a Lennox and it that case you could not. All boilers need to be vented with polypropylene.
|
|
|
|
|
|
#26 |
|
Senior Member
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
|
I didnt mean pvc specifically but plastic in general. You knew what I meant. These boilers will discharge flue temps of about 140 degrees which mean they dont need a mortar chimney.
__________________
SIKSUKR |
|
|
|
|
|
#27 | |
|
Senior Member
Join Date: Oct 2004
Location: Laconia NH
Posts: 5,669
Thanks: 3,282
Thanked 1,132 Times in 814 Posts
|
Quote:
As far as builders and developers are concerned, you are absolutely right about cutting cost. You will see inefficient HVAC on all new construction unless the homeowner request otherwise. I see a lot of homes built along an existing natural gas pipeline, not being hooked up. Builders do not want to go through the hassle and inspection of gas lines, but rather put in oil. Again unless the home owner asks. A lot of homeowners believe the latest RBC includes energy efficiency. Unfortunately it does not. Its up to the homeowners to work with the builders if they want 5 star efficiency. I talk to one well known builder/developer who claims to be the 'Premier Builder in the Lakes Region' about why the homes he build are not efficient. 'Why pay the additional expense, if the new owner is going to sell the home eventually. After all you can't take it with you and oil is cheap!'
__________________
Someday may never be an actual day. |
|
|
|
|
|
|
#28 | |
|
Senior Member
Join Date: Nov 2016
Location: Waltham Ma./Meredith NH
Posts: 4,429
Thanks: 2,431
Thanked 1,271 Times in 814 Posts
|
Quote:
|
|
|
|
|
|
|
#29 |
|
Senior Member
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,459
Thanks: 357
Thanked 126 Times in 100 Posts
|
|
|
|
|
|
|
#30 | |
|
Senior Member
Join Date: Jan 2007
Posts: 529
Thanks: 83
Thanked 194 Times in 118 Posts
|
Quote:
For those suggesting Rinaai wall hung water heaters, you need to understand that these have to be flushed yearly or you lose your warranty on the heat exchanger... unless you get someone to lie for you. These also are prone to the screen being plugged and poor water quality creating issues. Why would someone would pay over $3000 for a way to heat their water when they could get it done much cheaper and as cost effective, I'll never know and understand? |
|
|
|
|