Default Furnace Problem ?

SIKSUKR
Ignitier spark was marginal but OK, during first test, the Technician performed early in the morning, but when he came back later in the afternoon, after furnace went out again, there was litterally little if any spark, DOA !
Igniter was replaced Monday, today is Sat., and furnace appears to be running OK, at least it hasn't shudown, since new Igniter part was replaced.

You mentioned 'Transformer' ? That was replaced last Fall 2010.
So you're saying a bad Transformer will affect the amount of spark the Igniter module will create?

Kamper
My Burner Technician did that same test you described with Iignitor coil. LaMy tech did same, laying a screw driver across the 2 coil elemnets, to test the spark. Origianl Igniter proed to have no spark. Replacement Igniter spark was at least 1". Seem to do the trick.

As far as blower motor, replaced that previous Jan (2010) ! $$$


Thanks guys for all the valuable info., much appreciaited!

BD
bigdog is offline   Reply With Quote
Old 03-07-2011, 02:00 PM   #2
SIKSUKR
Senior Member
 
SIKSUKR's Avatar
 
Join Date: Apr 2004
Posts: 5,075
Thanks: 215
Thanked 903 Times in 509 Posts
Default

Quote:
Originally Posted by bigdog View Post
SIKSUKR

You mentioned 'Transformer' ? That was replaced last Fall 2010.
So you're saying a bad Transformer will affect the amount of spark the Igniter module will create?

BD
Oh yes. The transformer gives the ignitor, which is basically like a spark plug, the necessary voltage to generate that spark. It puts out somewhere around 10,000 volts.
__________________
SIKSUKR
SIKSUKR is offline   Reply With Quote
Old 05-08-2011, 05:59 PM   #3
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,468
Thanks: 373
Thanked 126 Times in 100 Posts
Default Furnace Problem ?

More furnace issues..... Or maybe just the same one?
FYI, this is an oil furnace heating by FHW.

Furnace just has never really never woked smoothly, for any long length of time. By that I mean like 2-3 weeks time. Over the winter, I've spent over $1000 on labor and parts, and I'm probably underestimating...

Since last year, I think I've replaced all the major components on the furnace, including 'powerr venter'. Latest issue was noticed upon recent arrival to house, after a one week absence. Furnace was off, so I pushed the 'reset button' on furnace, and it came on first attempt. Prior to this, thermostats on both floors of house were set around 55 degrees. After furnace came on, I set the thermostats at 60 degrees, and have left there. That was 2 days ago.

Just went to draw hot water and noticed it was 'luke-warm' !
Checked furnace, and it was 'off' ! @$*(@^$_*(@^*$_@*(^$#&*(^$*
Anyway, hit reset and furnace came on again.

I've had two different oil dealers service this furnace in the last year and a half. I've changed oil dealers b/c I didn't like the service I was given for one reason or another. Enough said ! These guys are suppose to be the
so-called experts, that's why they charge you $80-100 per hour.

I've explained the issue with furnace shutting down, to both oil dealers, and they both completely checked thw system, and cannot identify what is causing furnace to shut down at any given time.?

TG is Spingtime, and not threat of freezing can occur, especially when I may be away from property.

Probably going to seek another oil dealer service, maybe a third source will have a better idea, about furnace shutdown for no reason ?

#1 - Has anyone on the Forum experienced furnace issues as I've described?

#2 - Shouldn't I be able to lower my furnace to say 50-55 degree,
without the furnace shutting off? Or is there possibly some type fo 'low-limit' swithch on furnaces, that will shut down system automatically, if it reaches a low temp?

Any help or information is greatly apprecaited !

BD
bigdog is offline   Reply With Quote
Old 05-08-2011, 06:49 PM   #4
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Did your service people check the photo cell to see if it was dirty or not working? This will shut your burner down if not working properly or dirty. It will startup and run for an extended period of time but will shut down if it doesn’t see a flame.
If your burner is running rich it will clog up the photocell eye and shut the burner down. You can tell if your burner is running rich by looking at the nozzle and the cage around the nozzle. If they are black with soot it could cause a problem with the eye.

As you know the way oil burners work is oil is sprayed through a nozzle at high pressure (at least 100 psig) and is ignited by an electric spark from a high voltage transformer.
Once the oil starts burning there is either a photo cell to detect light from the flame or a thermostat in the stack (chimney) that detects heat from the fire and needs to see it within a certain period of time (usually 45) seconds or it will shut the burner off.
If the flame is not established the circuitry on the control properly called the "Primary" will activate an electric heater on a thermal relay that will pop open after the 45 second time period. After this happens you have to reset the control (after it cools) and you have another 45 seconds.
Newer controls may have an electronic system that gives you like 2 tries to get the oil burner started before it gives up then you must follow a procedure to clear the fault.
Rusty is offline   Reply With Quote
The Following 2 Users Say Thank You to Rusty For This Useful Post:
bigdog (05-08-2011), Kamper (05-09-2011)
Old 05-08-2011, 07:28 PM   #5
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,468
Thanks: 373
Thanked 126 Times in 100 Posts
Default Furnace Issue

Thanks Rusty, very informative feedback.

I know I don't have a thermostat in the stack chimney, so where is this "photo cell" located?

FYI, I have a fairly new Honeywell Primary Oil Control (R7184U) 9 months old, and Beckett Ignitor module, less than 3 mos. old. Contacts adjusted at time of installation.

Not sure if Ignitor or control chamber, or stack full os soot? Would think oil dealer(s) would have checked those things at the time parts were replaced
They're the experts right? I'm just the consumer, writing the checks !

Is the 'photo cell' located in or around the furnace chamber, or maybe in the
"Primary Oil Control " housing?

Thanks,
BD
bigdog is offline   Reply With Quote
Sponsored Links
Old 05-08-2011, 08:14 PM   #6
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,963
Thanks: 490
Thanked 704 Times in 394 Posts
Default

If the reset is tripped, then it is either not lighting or going out some time after it lights. I'd check the photo cell as Rusty suggests, make sure all connections are good (pull on wires that are in connectors (gently), they should not pull out of the connectors). Other problem could be air getting in the oil line, but the system would probably not restart if this were happening. If the photo eye is sooted up then the burner is not set correctly and needs to be adjusted. Obviously you've checked that you have enough oil in the tank.......
ITD is offline   Reply With Quote
Old 05-08-2011, 08:21 PM   #7
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,963
Thanks: 490
Thanked 704 Times in 394 Posts
Default

Manual on your controller.... http://www.forwardthinking.honeywell...ll/69_1459.pdf

Don't blow yourself up...
ITD is offline   Reply With Quote
Old 05-08-2011, 08:36 PM   #8
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,468
Thanks: 373
Thanked 126 Times in 100 Posts
Default Furnace Problem ?

Thanks ITD for link on Honeywell Controller.

BTW, the last time I hit reset button, I held in for about 10 seconds then released. After about 15-20 seconds the burner kiked on and a huge blast of black smoke, came out my power venter. I suspect as a reults of an accumulation of oil in the combustion chamber. Next time, I'll just hit the reset button and release immediately ! Can you say KA-BOOM ! Not funny !

FYI, service tech also replace wom type of swithc on the power vent recently. As you know, if the power venter is not working, you'll NEVER start the furnace. It's a built-in safety feature. Darn powere ventors, I hate them, lots of trouble.

Also, which I didn't mention, is the furnace is located in a small outside room
(8x3) attached to the main building, but definitely separate. Have been told that this furnace room space, may not be getting enough air-flow exchange into the area, which could cause a shut-down of furnace. Also I guess a possibility ? Sort of makes ense ?

Will check wires in control module and photo cell next.

Thanks,
BD
bigdog is offline   Reply With Quote
Old 05-08-2011, 09:09 PM   #9
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,963
Thanks: 490
Thanked 704 Times in 394 Posts
Default

From what you are describing I would suspect the ignitor system. The electrodes have to be located properly with the proper gap for the burner to light correctly, sounds like you have replaced most of the other parts although sometimes you get infant mortality.

If it were an issue with the power vent, the burner would not get the chance to light so the reset button would not get the chance to trip.

My guess anyway.

Page 5 of this manual shows the measurements for this particular model burner. It's important that they measure this with a gage or a ruler, a lot of guys just eyeball it......... I wouldn't mess with this unless you know how to open the burner up, but I wouldn't hesitate to look over the guy's shoulder and ask questions.

http://www.beckettcorp.com/protect/t...AF%20R0803.pdf
ITD is offline   Reply With Quote
Old 05-08-2011, 09:41 PM   #10
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,468
Thanks: 373
Thanked 126 Times in 100 Posts
Default Furnace Issue

ITD... FYI... the Ignitor module was repalced less than 3 mos ago. As you mentioned the space between the Ignitor terminals needs to be calibrated fairly accurately.

I think my service tech just 'eye-balled', as you described. He told me at the time, that he was the expert, and had been doing this for over 30 yrs, so didn't need to use gage. I took away arrogance from that remark !

"Ok" was my answer. Who was I to tell the expert how to do his job, or question his ability and experience, what do I know ! Well maybe he got the terminals gapped correctly, and maybe he didn't?

I'll check the Ignitor box for soot, and also check photo cell and clean.
I see on page# 5 where electrode terminals are described. I'm assuming there's a special tool you need to use to set that gap?

Thanks,
BD
bigdog is offline   Reply With Quote
Old 05-09-2011, 10:08 AM   #11
Rusty
Senior Member
 
Join Date: Oct 2010
Posts: 2,028
Thanks: 603
Thanked 687 Times in 425 Posts
Default

Quote:
Originally Posted by bigdog View Post
ITD... FYI... the Ignitor module was repalced less than 3 mos ago. As you mentioned the space between the Ignitor terminals needs to be calibrated fairly accurately.

I think my service tech just 'eye-balled', as you described. He told me at the time, that he was the expert, and had been doing this for over 30 yrs, so didn't need to use gage. I took away arrogance from that remark !

"Ok" was my answer. Who was I to tell the expert how to do his job, or question his ability and experience, what do I know ! Well maybe he got the terminals gapped correctly, and maybe he didn't?

I'll check the Ignitor box for soot, and also check photo cell and clean.I see on page# 5 where electrode terminals are described. I'm assuming there's a special tool you need to use to set that gap?

Thanks,
BD
I have a Carlin burner and it is under the transformer/primary control. When you flip it up you can see the CAD cell and it looks like this:

Rusty is offline   Reply With Quote
Old 05-09-2011, 10:31 AM   #12
VitaBene
Senior Member
 
VitaBene's Avatar
 
Join Date: Jul 2007
Location: Moultonborough
Posts: 3,648
Thanks: 1,747
Thanked 1,665 Times in 862 Posts
Default

Rusty has given you some great info.

Unfortunately, it seems like your technicians are not diagnosing the problem, but instead are throwing parts at it. This is usually a sign of someone who lacks good troubleshooting skills, perhaps you need to try a different company?
VitaBene is offline   Reply With Quote
Old 05-10-2011, 11:09 AM   #13
RLW
Senior Member
 
RLW's Avatar
 
Join Date: Jul 2002
Location: Alton Bay on the mountain by a lake
Posts: 2,023
Thanks: 563
Thanked 444 Times in 311 Posts
Default

Quote:
Originally Posted by bigdog View Post
ITD... FYI... the Ignitor module was repalced less than 3 mos ago. As you mentioned the space between the Ignitor terminals needs to be calibrated fairly accurately.

I think my service tech just 'eye-balled', as you described. He told me at the time, that he was the expert, and had been doing this for over 30 yrs, so didn't need to use gage. I took away arrogance from that remark !

"Ok" was my answer. Who was I to tell the expert how to do his job, or question his ability and experience, what do I know ! Well maybe he got the terminals gapped correctly, and maybe he didn't?

I'll check the Ignitor box for soot, and also check photo cell and clean.
I see on page# 5 where electrode terminals are described. I'm assuming there's a special tool you need to use to set that gap?

Thanks,
BD
If you had a half a** tech come into your house to service your burner 99.9% of all the suggestions given would have bee checked for proper service. I'm not sure there really is such a person as an EXPERT burner servicemen. Time makes knowledge, but defiantly not and expert.
__________________
There is nothing better than living on Alton Mountain & our grand kids visits.
RLW is offline   Reply With Quote
Old 05-10-2011, 02:57 PM   #14
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,468
Thanks: 373
Thanked 126 Times in 100 Posts
Default Furnace Issue?

ITW,

Couldn't agree with your comments more.......

Spent a lot of $$$ and getiing half-***** service.

Hopefully, the next "new guys" on site will resolve my issue. That's a big TBD.

BD
bigdog is offline   Reply With Quote
Old 05-11-2011, 09:03 PM   #15
SPT13
Senior Member
 
Join Date: Jan 2009
Location: Weymouth Ma/Gilford when I can!
Posts: 63
Thanks: 120
Thanked 7 Times in 7 Posts
Default

Bigdog,
have you called Weil McLean at all? I had a situation like yours yrs ago and after watching guys change parts and having the same issues I called the manufacturer. I told them the problem, and they recommended a local guy who knew the furnace like the back of his hand. He had me up and running soon with no issues. Good luck!
SPT13 is offline   Reply With Quote
The Following User Says Thank You to SPT13 For This Useful Post:
bigdog (05-11-2011)
Old 05-12-2011, 10:31 AM   #16
SAMIAM
Senior Member
 
Join Date: Apr 2004
Location: Moultonborough
Posts: 2,961
Thanks: 352
Thanked 1,732 Times in 614 Posts
Default

Lesson to be learned is...shop carefully for a service company.Get recommendations from friends and neighbors.Makes me crazy when I call for service and they send some lunkhead that doesn't know what he's doing.You pay a service charge,travel charge,gas surcharge,labor rates as high as $85 and outrageous mark up on parts only to find it's still not working.So you call them back and they try something else that fixes the problem ...or maybe not.You just keep paying for someone to experiment until they stumble on the solution.
Even had a refigeration guy charge me for 2 techs at $85/hr only to find out the guy had his 10 year old son with him running for tools.
We have great luck with Lakeside Plumbing for heating and plumbing issues.The usually get it right the first time.When you call their office you get a real person and the gals that answer the phone can diagnose as good as any of the techs.They show up when promised and have emergency service.
SAMIAM is offline   Reply With Quote
The Following 2 Users Say Thank You to SAMIAM For This Useful Post:
CateP (05-12-2011), VitaBene (05-12-2011)
Old 05-19-2011, 08:36 AM   #17
bigdog
Senior Member
 
bigdog's Avatar
 
Join Date: Apr 2006
Location: Central MA-Gilford
Posts: 1,468
Thanks: 373
Thanked 126 Times in 100 Posts
Default Furnace Issue ?

More feedback to Forum regarding furnace problem.....

Just checked 'photo-cell', and it appears to be brand new. The Beckett Igniter module was recently replaced, and it looks like the photo cell, came included new and packaged with that module. I did clean the photo cell eye, and checked all wires, and all appears to be fine.

Furnace will start, and run for a while, but at various intervals will shut down w/o reason?

Primary Control goes into a 'restricted/lock-out sttate, but seems I can always reset w/o issues. When I do reset and furnaces starts, I get a huge plume of black smoke, ejected out my power-venter. I suspect this as a result of built-up oil, inthe burner chamber which did not origianilly ignite?
Guessing?

Next step will be to call Weil McClain to get some input from them. Maybe mu issues, is something, common to this brand of furnace, that requires specific settings? Also have called another P & H contractor recommended by a Forum member, and will be coming to house to review the issue.

Thanks,
Bigdog
bigdog is offline   Reply With Quote
Old 05-19-2011, 02:37 PM   #18
ITD
Senior Member
 
ITD's Avatar
 
Join Date: Apr 2004
Location: Moultonboro, NH
Posts: 2,963
Thanks: 490
Thanked 704 Times in 394 Posts
Default

If you checked the cad cell, you were a couple of steps away from removing the nozzle/electrode assy. If you are comfortable, you can give this a try, I'm thinking the electrodes are bad or more likely from your prior description of how it was installed last time, just not installed correctly. Good luck, don't blow yourself up.
ITD is offline   Reply With Quote
Old 05-23-2011, 08:58 PM   #19
sparky63
Junior Member
 
Join Date: May 2004
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by bigdog View Post
More feedback to Forum regarding furnace problem.....

Just checked 'photo-cell', and it appears to be brand new. The Beckett Igniter module was recently replaced, and it looks like the photo cell, came included new and packaged with that module. I did clean the photo cell eye, and checked all wires, and all appears to be fine.

Furnace will start, and run for a while, but at various intervals will shut down w/o reason?

Primary Control goes into a 'restricted/lock-out sttate, but seems I can always reset w/o issues. When I do reset and furnaces starts, I get a huge plume of black smoke, ejected out my power-venter. I suspect this as a result of built-up oil, inthe burner chamber which did not origianilly ignite?
Guessing?

Next step will be to call Weil McClain to get some input from them. Maybe mu issues, is something, common to this brand of furnace, that requires specific settings? Also have called another P & H contractor recommended by a Forum member, and will be coming to house to review the issue.

Thanks,
Bigdog
Hi Bigdog
Im a tech for a large oil company . from what you are discribing everything is working right up to the point of ingition ( I get a huge plume of black smoke, ejected out my power-venter.) you need 3 things to make combustion you also need them in the right amounts to much air will lean out the mixture to the point of not firing. to little spark will also not let it fire
sparky63 is offline   Reply With Quote
Old 05-23-2011, 09:02 PM   #20
sparky63
Junior Member
 
Join Date: May 2004
Posts: 4
Thanks: 0
Thanked 0 Times in 0 Posts
Default

bigdog pm me mby i can help i'm not much for typing
sparky63 is offline   Reply With Quote
Reply

Bookmarks

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -4. The time now is 12:52 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2026, vBulletin Solutions Inc.

This page was generated in 0.12642 seconds