Yikes is right, with that outlet damage so close to unprotected EPS foam nearby. You might think about protecting that foam with something. Current code says:
"...all foam plastic insulation must be separated from the interior of the building by an approved 15-minute thermal barrier, such as ½-inch gypsum wall board or equivalent material. This thermal barrier may be omitted if certain conditions are met in attics and crawl spaces. Specifically, entry must be restricted to service of utilities AND the foam plastic must be protected from ignition with a code specified material.

Section 316.5.3 of the IRC prescriptively defines the
following six materials as ignition barriers:
• 1½” mineral fiber insulation
• ¼” wood structural panels
• ⅜” particleboard
• ¼” hardboard
• ⅜” gypsum wall board
• 16 mil corrosion resistant steel
DickR is offline   Reply With Quote
 

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On

Forum Jump


All times are GMT -4. The time now is 05:41 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2026, vBulletin Solutions Inc.

This page was generated in 0.12389 seconds