Quote:
Originally Posted by SailinAway View Post
Here are some photos. I have more if there's something specific you want to see. The service card is from the first technician. The second one didn't leave a service card.
That's not a combustion test! The only way for sure you know one was done is with a printout from the combustion analyzer. They shouldn't have had any issue opening that up. The HB Smith is cleaned from the side panel. Make sure the side plates are lined up properly. Lift up that side panel, turn the heat up all the way to fire the boiler, go down stairs in front of where the panel was, shut off the lights, and see if you can see any flame or light. It doesn't say what nozzle , filter , strainer, he used or anything he did. Did he actually brush the boiler pins, remove the smoke pipe, vacuum the breech and smoke pipe and inspect the chimney to make sure it wasn't blocked? there's no proof he did any of those things except what he told you.